  1. What is the maximum allowable distance between sprinkler heads in a standard light hazard occupancy per NFPA 13?

    Answer: 15 feet

    NFPA 13 allows a maximum of 15 feet between sprinkler heads in light hazard occupancies.

  2. Which type of fire detection system continuously monitors the rate of temperature rise in a protected area?

    Answer: Rate-of-rise heat detector

    Rate-of-rise heat detectors activate when temperature increases faster than a set rate, typically 12–15°F per minute.

  3. Under NFPA 72, what is the minimum audible alarm level required in sleeping areas?

    Answer: 75 dB

    NFPA 72 requires a minimum of 75 dB at the pillow level in sleeping areas to ensure occupants are awakened.

  4. A dry-pipe sprinkler system is most appropriate for which environment?

    Answer: Areas subject to freezing temperatures

    Dry-pipe systems use pressurized air or nitrogen instead of water, preventing freezing in cold environments.

  5. What is the primary function of a fire damper in an HVAC system?

    Answer: Close automatically to stop fire spread through ductwork

    Fire dampers close automatically when a fusible link melts, preventing fire from traveling through HVAC ductwork.

  6. Which class of standpipe system requires that hose and nozzle equipment be provided and maintained by the building owner?

    Answer: Class II

    Class II standpipe systems are intended for use by building occupants and must include hose, rack, and nozzle.

  7. When testing a fire pump, the pump must deliver 150% of its rated capacity at what minimum percentage of rated pressure?

    Answer: 65%

    Per NFPA 20, a fire pump must deliver 150% of rated flow at no less than 65% of rated pressure.