PC Grounding and Bonding 2 — Questions and Answers
Question 1: According to NEC Article 250, what is the minimum size copper equipment grounding conductor required for a 100A circuit protected by a 100A breaker?
- #8 AWG (Correct answer)
- #6 AWG
- #4 AWG
- #10 AWG
Correct answer: #8 AWG
NEC Table 250.122 requires a minimum #8 AWG copper EGC for circuits with overcurrent protection rated at 100A.
Question 2: Which of the following locations requires a grounding electrode system to include a ground ring if no other electrode is available?
- Residential service panels under 200A
- Buildings with concrete-encased electrodes already installed
- Buildings or structures where no other electrode type exists on-site (Correct answer)
- Commercial occupancies over 1000 sq ft
Correct answer: Buildings or structures where no other electrode type exists on-site
NEC 250.52(A)(4) allows a ground ring as a grounding electrode when other electrode types are unavailable at the structure.
Question 3: What is the primary purpose of bonding in an electrical system?
- To provide a return path for fault current to the source
- To establish electrical continuity between conductive parts to eliminate voltage differences (Correct answer)
- To reduce the grounding electrode resistance to earth
- To protect equipment from lightning surges
Correct answer: To establish electrical continuity between conductive parts to eliminate voltage differences
Bonding ensures electrical continuity between conductive parts so no dangerous voltage differences exist between them.
Question 4: A concrete-encased electrode (Ufer ground) must contain at least how many feet of bare or zinc-galvanized steel reinforcing bars or rods?
- 10 feet
- 20 feet (Correct answer)
- 50 feet
- 100 feet
Correct answer: 20 feet
NEC 250.52(A)(3) requires at least 20 feet of steel reinforcing bar or rod encased in concrete for a Ufer ground.
Question 5: When installing a grounding electrode conductor in a metal raceway, what additional requirement applies?
- The raceway must be bonded to the grounding electrode conductor at both ends (Correct answer)
- The raceway must be PVC-coated to prevent corrosion
- The raceway must be at least 1-inch trade size
- The raceway must contain only the grounding conductor, no other wiring
Correct answer: The raceway must be bonded to the grounding electrode conductor at both ends
NEC 250.64(E) requires that when a GEC is installed in metal raceway, the raceway must be bonded to the GEC at both ends to prevent inductive choke.
Question 6: Which NEC article specifically addresses grounding and bonding requirements?
- Article 200
- Article 230
- Article 250 (Correct answer)
- Article 280
Correct answer: Article 250
NEC Article 250 covers all grounding and bonding requirements for electrical installations.
Question 7: In a separately derived system (e.g., a transformer), where must the system bonding jumper be installed?
- At the first overcurrent device downstream
- At the grounding electrode only
- At the source of the separately derived system (Correct answer)
- At the main service entrance
Correct answer: At the source of the separately derived system
NEC 250.30(A)(1) requires the system bonding jumper to be installed at the source of the separately derived system.
According to NEC Article 250, what is the minimum size copper equipment grounding conductor required for a 100A circuit protected by a 100A breaker?