NABCEP Commissioning and Troubleshooting 2 — Questions and Answers
Question 1: During PV system commissioning, you measure an open-circuit voltage significantly higher than the STC-rated Voc. What is the most likely cause?
- Shading on one or more modules
- Ambient temperature is much lower than 25°C STC (Correct answer)
- A bypass diode has failed short
- The inverter is in sleep mode
Correct answer: Ambient temperature is much lower than 25°C STC
PV module Voc increases as temperature decreases below 25°C STC, so cold conditions yield higher-than-rated Voc readings.
Question 2: A string of 10 modules shows an Isc that is 15% lower than expected while all other strings test normally. What is the first diagnostic step?
- Replace the string combiner fuse
- Inspect each module in the string for shading or soiling (Correct answer)
- Reprogram the inverter MPPT settings
- Check the AC output voltage at the main panel
Correct answer: Inspect each module in the string for shading or soiling
A proportionally low Isc in a single string commonly points to shading, soiling, or a failing module reducing current generation.
Question 3: When commissioning a battery-based off-grid system, what parameter must be verified to ensure the charge controller protects the battery bank?
- Maximum PV array open-circuit voltage vs. charge controller input rating (Correct answer)
- AC output frequency set to 60 Hz
- Nominal battery voltage matches the inverter output voltage
- Ground fault detection threshold on the inverter
Correct answer: Maximum PV array open-circuit voltage vs. charge controller input rating
The PV array Voc at minimum temperature must not exceed the charge controller's maximum input voltage rating to prevent damage.
Question 4: An inverter repeatedly faults with an 'AC voltage high' error during afternoon peak. What is the most probable cause?
- The DC input voltage is too low
- Utility grid voltage rises above the inverter's upper trip threshold (Correct answer)
- The inverter needs a firmware update
- PV modules are overheating
Correct answer: Utility grid voltage rises above the inverter's upper trip threshold
Backfeed from distributed generation during low-load periods can raise local utility voltage, triggering AC overvoltage faults.
Question 5: During commissioning, an IR thermal scan of a module shows one cell running 20°C hotter than surrounding cells. What does this indicate?
- The module has the highest irradiance exposure
- A localized cell defect such as a crack or hot spot (Correct answer)
- The bypass diode is operating correctly
- Soiling on the module surface
Correct answer: A localized cell defect such as a crack or hot spot
An isolated hot cell in an IR scan is a classic sign of a cracked or defective cell creating a resistive hot spot.
Question 6: What is the correct procedure when an electrolytic capacitor is suspected of failing inside an inverter?
- Power cycle the inverter three times to reset it
- De-energize the inverter, wait the manufacturer's specified discharge time, then inspect (Correct answer)
- Measure capacitor voltage while the inverter is operating
- Replace the inverter's DC disconnect and retest
Correct answer: De-energize the inverter, wait the manufacturer's specified discharge time, then inspect
Capacitors store dangerous charge; the inverter must be de-energized and fully discharged before any internal inspection.
Question 7: A grid-tied PV system produces less energy than modeled but all electrical measurements appear normal. What non-electrical factor should be investigated?
- String fusing size
- Actual site shading vs. design assumptions (Correct answer)
- Inverter transformer tap setting
- Ground electrode resistance
Correct answer: Actual site shading vs. design assumptions
Discrepancies between modeled and actual energy production often stem from shading sources (trees, chimneys) not captured in the original design.
During PV system commissioning, you measure an open-circuit voltage significantly higher than the STC-rated Voc.
What is the most likely cause?