Licensed Electrical Contractor NEC General Requirements 3 — Questions and Answers
Question 1: Per NEC 110.26(A)(1), what is the minimum clear working space depth in front of equipment operating at 151–600V to ground with exposed live parts on one side and a grounded surface on the other (Condition 2)?
- 3 feet
- 3.5 feet (Correct answer)
- 4 feet
- 4.5 feet
Correct answer: 3.5 feet
NEC Table 110.26(A)(1) specifies 3.5 feet (42 inches) of working clearance for 151–600V Condition 2.
Question 2: What does NEC 110.22 require to be legibly marked on disconnecting means?
- The installer's name and license number
- The load served and the source of supply (Correct answer)
- The ampere rating and voltage rating only
- The date of installation and inspection
Correct answer: The load served and the source of supply
NEC 110.22 requires each disconnecting means to be legibly marked to indicate the load served and its source of supply.
Question 3: According to NEC 110.12, electrical equipment must be installed in a:
- Listed enclosure only
- Neat and workmanlike manner (Correct answer)
- Location accessible only to qualified persons
- Dry location unless weatherproof rated
Correct answer: Neat and workmanlike manner
NEC 110.12 requires all electrical equipment to be installed in a neat and workmanlike manner.
Question 4: Under NEC 110.14(C)(1), the temperature rating of a conductor connected to a 60°C-rated terminal on a device rated 100A or less must be based on:
- 75°C ampacity tables
- 90°C ampacity tables
- 60°C ampacity tables (Correct answer)
- The highest rated insulation available
Correct answer: 60°C ampacity tables
NEC 110.14(C)(1) requires that conductors connected to 60°C-rated terminals on equipment 100A or less be sized using the 60°C ampacity column.
Question 5: What is the NEC definition of a 'qualified person'?
- A licensed electrician with 5+ years of experience
- One who has skills and knowledge related to the construction and operation of electrical equipment and installations (Correct answer)
- Any person with an electrical contractor license
- A journeyman electrician approved by the AHJ
Correct answer: One who has skills and knowledge related to the construction and operation of electrical equipment and installations
The NEC Article 100 definition of a qualified person is one who has skills and knowledge related to the construction and operation of electrical equipment and has received safety training.
Question 6: NEC 110.10 requires that the components of a circuit be selected so that the circuit's impedance characteristics allow the overcurrent device to:
- Trip within 3 cycles under any condition
- Clear fault current without extensive damage to components (Correct answer)
- Limit fault current to 10,000A maximum
- Coordinate with downstream devices at all times
Correct answer: Clear fault current without extensive damage to components
NEC 110.10 requires circuit components to be selected to permit the overcurrent device to clear a fault without extensive damage to electrical components.
Question 7: Per NEC 110.26(D), when is dedicated electrical space required above panelboards and switchboards?
- Only in commercial occupancies
- For all equipment rated over 1200A
- For the width and depth of the equipment from the floor to a height of 6 feet above or to the structural ceiling, whichever is lower (Correct answer)
- Only when equipment is located outdoors
Correct answer: For the width and depth of the equipment from the floor to a height of 6 feet above or to the structural ceiling, whichever is lower
NEC 110.26(D) requires dedicated electrical space from the floor to 6 feet above the equipment or to the structural ceiling for panelboards and switchboards.
Per NEC 110.26(A)(1), what is the minimum clear working space depth in front of equipment operating at 151–600V to ground with exposed live parts on one side and a grounded surface on the other (Condition 2)?