Licensed Electrical Contractor Code, Theory, and Calculations 3 — Questions and Answers
Question 1: What NEC section governs the installation of conductors in raceways, and what is the maximum fill percentage for a single conductor in a conduit?
- NEC 358.22 — 53%
- NEC 344.22 — 31%
- NEC 310.15 — 40%
- NEC 300.17 — 53% (Correct answer)
Correct answer: NEC 300.17 — 53%
NEC 300.17 references Chapter 9 Table 1, which allows 53% fill for a single conductor in a conduit.
Question 2: What is the reactance of a 60 Hz circuit with an inductance of 0.5 H?
- 188.5 Ω (Correct answer)
- 94.2 Ω
- 376.9 Ω
- 30 Ω
Correct answer: 188.5 Ω
Inductive reactance XL = 2πfL = 2π × 60 × 0.5 ≈ 188.5 Ω.
Question 3: Under NEC 210.8(A), GFCI protection is required for all 125 V, 15 A and 20 A receptacles in which residential location?
- All outdoor locations (Correct answer)
- Living room only
- Bedrooms only
- Attic storage areas only
Correct answer: All outdoor locations
NEC 210.8(A) requires GFCI protection for all 125 V, 15 A and 20 A receptacles installed in outdoor locations of dwelling units.
Question 4: A 480 V, 3-phase, 4-wire wye system has a line-to-neutral voltage of approximately:
- 277 V (Correct answer)
- 240 V
- 208 V
- 347 V
Correct answer: 277 V
Line-to-neutral voltage = line voltage ÷ √3 = 480 ÷ 1.732 ≈ 277 V.
Question 5: Per NEC 250.122, the minimum size equipment grounding conductor (EGC) for a circuit protected by a 200 A overcurrent device is:
- 6 AWG copper (Correct answer)
- 4 AWG copper
- 8 AWG copper
- 2 AWG copper
Correct answer: 6 AWG copper
NEC Table 250.122 specifies a minimum 6 AWG copper EGC for circuits protected by overcurrent devices up to 200 A.
Question 6: In a capacitive AC circuit, the current:
- Leads the voltage by 90° (Correct answer)
- Lags the voltage by 90°
- Is in phase with voltage
- Leads the voltage by 45°
Correct answer: Leads the voltage by 90°
In a purely capacitive circuit, current leads voltage by 90° because the capacitor charges before the voltage peaks.
Question 7: NEC 408.36 requires panelboards supplied by a 4-wire delta system to be labeled to indicate the:
- High-leg (wild leg) conductor and its voltage to ground (Correct answer)
- Total panel ampacity rating
- Number of branch circuits permitted
- Grounding conductor size
Correct answer: High-leg (wild leg) conductor and its voltage to ground
NEC 408.36 requires the high-leg (wild leg) of a 4-wire delta system to be durably marked at the panelboard to indicate its higher voltage to ground (typically 208 V).
What NEC section governs the installation of conductors in raceways, and what is the maximum fill percentage for a single conductor in a conduit?