Journeyman Electrician’s Exam Journeyman Electrician's Overcurrent Protection 3 — Questions and Answers
Question 1: Where must an overcurrent device be located relative to the point where a conductor receives its supply?
- Within 6 feet of the supply point
- At the point where the conductor receives its supply (Correct answer)
- At the load end of the conductor
- Within 10 feet of the supply point
Correct answer: At the point where the conductor receives its supply
NEC 240.21 requires OCPDs to be placed at the point where the conductor receives its supply unless a tap rule exception applies.
Question 2: A feeder tap conductor using the 10-foot tap rule must have an ampacity of at least what percentage of the overcurrent device protecting the feeder?
- 100%
- 33% (Correct answer)
- 10%
- 50%
Correct answer: 33%
NEC 240.21(B)(1) requires the tap conductor's ampacity to be at least one-third (33%) of the feeder OCPD rating for the 10-foot tap rule.
Question 3: Which of the following best describes an 'inverse-time' circuit breaker?
- It trips faster as the current increases (Correct answer)
- It trips at a fixed time regardless of current
- It trips only on ground faults
- It trips only when current drops below rated value
Correct answer: It trips faster as the current increases
An inverse-time breaker has a trip time that decreases as the overcurrent magnitude increases, providing time-current coordination.
Question 4: A fused disconnect for an air-conditioning unit must be installed within sight of and readily accessible from the unit. Which article covers this requirement?
- Article 230
- Article 240
- Article 440 (Correct answer)
- Article 430
Correct answer: Article 440
NEC Article 440 covers air-conditioning and refrigerating equipment, including the disconnecting means and overcurrent protection requirements.
Question 5: What is the maximum OCPD size allowed for a 15 AWG copper conductor used in a branch circuit?
- 10 amperes
- 15 amperes (Correct answer)
- 20 amperes
- 25 amperes
Correct answer: 15 amperes
NEC 240.4(D)(3) limits the OCPD for 14 AWG to 15A; 15 AWG is not a standard branch-circuit size, so 14 AWG rules (15A max) apply.
Question 6: Ground-fault circuit interrupter (GFCI) protection detects current imbalances as small as:
- 5 milliamperes (±1 mA) (Correct answer)
- 15 milliamperes
- 30 milliamperes
- 100 milliamperes
Correct answer: 5 milliamperes (±1 mA)
GFCI devices are designed to trip when they sense a ground-fault current of approximately 4–6 mA (nominally 5 mA ±1 mA).
Question 7: Which conductor is NOT required to be protected by an overcurrent device under NEC 240.22?
- Grounded (neutral) conductors (Correct answer)
- Ungrounded phase conductors
- Travelers in 3-way switch circuits
- Equipment grounding conductors
Correct answer: Grounded (neutral) conductors
NEC 240.22 prohibits placing an OCPD in series with the grounded conductor unless the device opens all conductors simultaneously.
Where must an overcurrent device be located relative to the point where a conductor receives its supply?