Journeyman Electrician’s Exam Journeyman Electrician's 5 — Questions and Answers
Question 1: According to the NEC, what is the maximum distance between supports for rigid nonmetallic conduit (PVC) with a trade size of 1 inch?
- 3 feet
- 4 feet (Correct answer)
- 5 feet
- 6 feet
Correct answer: 4 feet
NEC Table 352.30(B) requires PVC conduit of 1-inch trade size to be supported at maximum intervals of 4 feet.
Question 2: What is the maximum number of 90-degree bends permitted in a single conduit run between pull points?
- 2
- 3
- 4 (Correct answer)
- 360 degrees total
Correct answer: 4
NEC 358.26 (and similar articles) limit the total bends between pull points to 360 degrees, which equals four 90-degree bends.
Question 3: Which of the following loads is considered a continuous load for circuit sizing purposes?
- A refrigerator cycling on and off
- A lighting circuit energized for 8 hours per day (Correct answer)
- A motor running for 2.5 hours
- A toaster oven used for 30 minutes
Correct answer: A lighting circuit energized for 8 hours per day
NEC 100 defines a continuous load as one where the maximum current is expected to continue for 3 hours or more; 8 hours of lighting qualifies.
Question 4: What is the required working clearance in front of a 120/240V panelboard mounted in a residential garage?
- 18 inches
- 24 inches
- 30 inches (Correct answer)
- 36 inches
Correct answer: 30 inches
NEC 110.26(A)(1) requires a minimum working clearance of 3 feet (36 inches) in front of electrical equipment rated 120V to 250V, Condition 1.
Question 5: When calculating service load for a residential dwelling, what demand factor applies to the first 3,000 VA of general lighting load?
- 25%
- 50%
- 75%
- 100% (Correct answer)
Correct answer: 100%
NEC Table 220.42 requires the first 3,000 VA of general lighting load in a dwelling unit to be calculated at 100% demand factor.
Question 6: In a commercial location, GFCI protection for 125-volt, 15- and 20-ampere receptacles is required in which area?
- Storage rooms only
- All areas accessible to the public
- Kitchens, bathrooms, rooftops, and other specified locations (Correct answer)
- Only outdoors
Correct answer: Kitchens, bathrooms, rooftops, and other specified locations
NEC 210.8(B) requires GFCI protection for commercial receptacles in kitchens, bathrooms, rooftops, outdoors, sinks, and other specific locations.
Question 7: What is the power factor of a purely resistive circuit?
- 0
- 0.5
- 0.8
- 1.0 (Correct answer)
Correct answer: 1.0
A purely resistive circuit has voltage and current in phase, so the power factor equals 1.0 (unity), meaning all power is real (active) power.
According to the NEC, what is the maximum distance between supports for rigid nonmetallic conduit (PVC) with a trade size of 1 inch?