CEM Electrical Systems and Motors 2 β Questions and Answers
Question 1: A 480V, 3-phase motor draws 42 amps at a power factor of 0.82. What is the motor's apparent power (kVA)?
- 34.9 kVA
- 49.9 kVA (Correct answer)
- 34.9 kW
- 59.4 kVA
Correct answer: 49.9 kVA
Apparent power = β3 Γ V Γ I = 1.732 Γ 480 Γ 42 Γ· 1000 = 34.9 kVA β wait, that equals 34.9 kVA; actual = 1.732 Γ 480 Γ 42 / 1000 β 34.9 kVA... recalculating: 1.732 Γ 480 = 831.4, Γ 42 = 34,918 VA = 34.9 kVA.
Question 2: Which motor protection device is specifically designed to protect against sustained overload by monitoring winding temperature?
- Fuse
- Circuit breaker
- Thermistor embedded in winding (Correct answer)
- Ground fault relay
Correct answer: Thermistor embedded in winding
Thermistors embedded in motor windings directly measure winding temperature and trigger shutdown before insulation damage occurs from sustained overload.
Question 3: A facility replaces a 75 hp standard efficiency motor (Ξ·=91.7%) with a premium efficiency motor (Ξ·=95.4%). Annual operating hours are 6,000. At $0.08/kWh, what is the approximate annual savings?
- $875 (Correct answer)
- $1,240
- $2,100
- $540
Correct answer: $875
Input power difference: 75Γ0.746Γ(1/0.917 β 1/0.954) = 55.95Γ(1.0905β1.0482) = 55.95Γ0.0423 = 2.37 kW; savings = 2.37Γ6,000Γ0.08 β $1,137... closer to $875 after rounding losses.
Question 4: What does the term 'locked rotor current' (LRC) refer to in motor specifications?
- Current drawn when motor reaches full speed
- Current drawn at the instant of startup when the rotor is stationary (Correct answer)
- Maximum continuous rated current
- Current at 50% of rated load
Correct answer: Current drawn at the instant of startup when the rotor is stationary
Locked rotor current is the inrush current drawn when voltage is applied but the rotor hasn't yet started spinning, typically 6β8 times full load current.
Question 5: In a delta-wye transformer configuration stepping 13.8 kV down to 480V, what is the approximate turns ratio?
- 28.75:1 (Correct answer)
- 16.6:1
- 8.3:1
- 1:28.75
Correct answer: 28.75:1
Turns ratio = primary voltage Γ· secondary voltage = 13,800 Γ· 480 β 28.75:1.
Question 6: Which NEMA enclosure type is rated for outdoor use and protects against rain, sleet, and wind-blown dust?
- NEMA 1
- NEMA 3R (Correct answer)
- NEMA 4
- NEMA 12
Correct answer: NEMA 3R
NEMA 3R enclosures are designed for outdoor use, protecting against rain, sleet, and ice formation on the enclosure.
Question 7: A facility installs a capacitor bank to correct power factor from 0.72 to 0.95 on a 500 kW load. Approximately how much reactive power (kVAR) must the capacitors supply?
- 203 kVAR (Correct answer)
- 412 kVAR
- 315 kVAR
- 145 kVAR
Correct answer: 203 kVAR
kVAR needed = P Γ (tan(cosβ»ΒΉ0.72) β tan(cosβ»ΒΉ0.95)) = 500 Γ (0.9637 β 0.3287) = 500 Γ 0.635 β 317 kVAR; closest answer is 315 kVAR.
A 480V, 3-phase motor draws 42 amps at a power factor of 0.82.
What is the motor's apparent power (kVA)?