CEI Electrical Code & Standards 2 — Questions and Answers
Question 1: Under the NEC, what is the maximum allowed voltage drop for branch circuits to ensure reasonable efficiency of operation?
- 1%
- 2%
- 3% (Correct answer)
- 5%
Correct answer: 3%
NEC 210.19(A) informational note recommends limiting branch circuit voltage drop to 3% for reasonable efficiency.
Question 2: Which NEC article governs the installation of patient care areas in health care facilities?
- Article 517 (Correct answer)
- Article 518
- Article 520
- Article 525
Correct answer: Article 517
NEC Article 517 covers electrical wiring and equipment installed in health care facilities including patient care areas.
Question 3: According to the NEC, a 20-ampere, 125-volt receptacle installed outdoors must be protected by which of the following?
- AFCI
- GFCI (Correct answer)
- Surge protector
- Double-pole breaker
Correct answer: GFCI
NEC 210.8(A) requires GFCI protection for 125-volt receptacles installed in outdoor locations.
Question 4: What is the minimum clearance required by the NEC between the top of a service entrance conductor and a window that opens?
- 2 feet
- 3 feet (Correct answer)
- 4 feet
- 6 feet
Correct answer: 3 feet
NEC 230.9(A) requires service conductors to be at least 3 feet from windows that open.
Question 5: Which NEC article specifically addresses the installation of solar photovoltaic (PV) systems?
- Article 690 (Correct answer)
- Article 695
- Article 700
- Article 705
Correct answer: Article 690
NEC Article 690 covers the installation of solar photovoltaic energy systems.
Question 6: Under NEC 300.4, where a raceway or cable passes through a wood structural member, a steel plate of at least what thickness is required when the edge is within 1-1/4 inches of the nearest edge?
- 1/16 inch
- 1/8 inch (Correct answer)
- 1/4 inch
- 3/8 inch
Correct answer: 1/8 inch
NEC 300.4(A)(1) requires a steel plate at least 1/8 inch thick to protect cables or raceways from nails and screws.
Question 7: The NEC requires that equipment grounding conductors be identified by which color when insulated?
- White or gray
- Green or bare (Correct answer)
- Black or red
- Orange or yellow
Correct answer: Green or bare
NEC 250.119 requires equipment grounding conductors to be identified by green insulation, green with yellow stripe, or bare copper.
Under the NEC, what is the maximum allowed voltage drop for branch circuits to ensure reasonable efficiency of operation?